Alphacool NexXxoS XT45 Full Copper 1260mm SuperNova and quick disconnect

Feel free to ask anytime, no worries.
They all come out pretty much the same. Strictly speaking, only the Panama has slightly more resistance, but the difference is minimal and barely measurable. Compared to the 17069, the ES slot bracket (5100099) shows no difference at all in flow restriction.
 
Feel free to ask anytime, no worries.
They all come out pretty much the same. Strictly speaking, only the Panama has slightly more resistance, but the difference is minimal and barely measurable. Compared to the 17069, the ES slot bracket (5100099) shows no difference at all in flow restriction.
Thanks, Eddy. I’ll take advantage of your willingness to help once again! The thing is, I keep coming up with new ideas every time.

What if I avoided using the Panama fitting or anything similar and instead routed the pipes through holes? That should help me avoid unnecessary restrictions, but would it make a noticeable difference?

If it would, I’ll go ahead with that solution. Otherwise, having unsecured pipes running through holes might not be the best option.

What do you think?
 
Whether you route the tubing through holes or use the ES pass-through bracket makes no difference. Even with the Panama bracket, you’ll barely notice a difference. And running tubing over metal edges certainly isn’t a good idea.

What exactly are you trying to achieve with these questions? More flow? Your cooling loop really doesn’t care whether you’re running 100 or 120 L/h. That might change your temperatures by around 0.5°C. In servers, we often run at just 60 L/h, while transferring more heat than any home PC produces. A little more or less flow in a loop really doesn’t matter much.
 
Whether you route the tubing through holes or use the ES pass-through bracket makes no difference. Even with the Panama bracket, you’ll barely notice a difference. And running tubing over metal edges certainly isn’t a good idea.

What exactly are you trying to achieve with these questions? More flow? Your cooling loop really doesn’t care whether you’re running 100 or 120 L/h. That might change your temperatures by around 0.5°C. In servers, we often run at just 60 L/h, while transferring more heat than any home PC produces. A little more or less flow in a loop really doesn’t matter much.
Since I'll be using just one pump, the VPP Apex (which I think is fantastic), I'm worried I'll have to run it at high speeds given the SuperNova, CPU, and GPU. So I was looking to minimize flow restrictions as much as possible.
 
I understand, but however you route the tubing out of the case, it won’t have a meaningful impact on your flow rate. Choosing the right quick-disconnect fittings is more important, if you’re using any. The number of bends and angled fittings in the loop also matters, the fewer there are, the better the flow.

Ultimately, the question is what flow rate you’re aiming for. Above around 75 L/h, the performance of our water blocks doesn’t change very much, as they are designed to work with relatively low flow rates. Whether you end up with 100 or 140 L/h makes practically no meaningful difference. High flow rates were needed in the past, when most water blocks didn’t yet use modern jet impingement technology.
 